I have just installed a IN-7 gas fired standing pilot-low water prob boiler. The house is a 1 pipe system. I still have all the old vents on the system. The vents are Hoffman #2 vacuum type. and the mains are Hoffman#16 vacuum vents.
All radiators are getting hot, and the system is quiet. I keep the old pressure gage which reads vacuum. On a cool down cycle I can read (-6 to -8)lbs of pressure (vacuum), the PressureTrol is set at 2 lb /1.5 lb. Is this the most efficient system to operate the new boiler on?
All radiators are getting hot, and the system is quiet. I keep the old pressure gage which reads vacuum. On a cool down cycle I can read (-6 to -8)lbs of pressure (vacuum), the PressureTrol is set at 2 lb /1.5 lb. Is this the most efficient system to operate the new boiler on?
0
Comments
-
The 2 PSI is a tad high,
and that particular system cries out for a vaporstat.
The new model Honeywell has (I forget the exact model number) would be the match made in heaven, control-wise for you.
Your system is designed to run at one PSI tops! I would suggest getting into the 1-PSI mode ASAP. The existing controller is going to cost fuel-wise - what the correct vaporstat will save in a year or less.
I urge you to make the change while it's straight forward, and little is rusted "tight."
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
What do you think about the vacuum vents? How do they play into the vaporstat?
Dan0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 103 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 936 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements