I=B=R Ratings

George T
George T Member Posts: 9
After a heat loss is done, which BTU output rating is used? I have seen conflicting info on different websites, even from Weil-Mcclain themselves. Various people claim to use the I=B=R Rating others claim to use the DOE Rating, including Weil themselves.


CGI - 6 Weil Boiler Specs
Input - 167 MBH
DOE Heating Capacity - 140 MBH
Net I=B=R Water rating - 122 MBH
If you us the IBR its an almost 20,000 btu difference, so which is correct???

Comments

  • Brad White
    Brad White Member Posts: 2,399
    For greatest efficiency

    I would use the gross output rating when sizing a hot water boiler. Most boilers are over-sized to begin with. To add 15% on top of that (ostensibly for piping and pick-up) is folly.

    The I=B=R 15% factor was originally conceived to account for piping and pick-up losses. These days with rational insulation and intelligent setbacks, few houses have to heat up from zero.
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"



    -Ernie White, my Dad
  • George T
    George T Member Posts: 9
    calification

    the house is 50 years of, has a single monoflo system which will be split to 2 maybe 3 zones. House is brick with full 2x4 inside constuction, and has some insulation.

    So you are saying i should use the DOE not IBR??
  • Brad White
    Brad White Member Posts: 2,399
    Yes

    I would use the DOE rating.
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"



    -Ernie White, my Dad