Max pressure on old Burnham cast iron baseboards
Hydrostatic Test pressure is 30 psi. But that is with water and not air. It is not recommended that you use air for testing. This is addressed on page 11 of the I&O manual. here is a link to that manual.
http://www.burnham.com/PDF/baseray_I&O.pdf
Glenn Stanton
Manager of Technical Development
Burnham Hydronics
U.S. Boiler Co., Inc.
http://www.burnham.com/PDF/baseray_I&O.pdf
Glenn Stanton
Manager of Technical Development
Burnham Hydronics
U.S. Boiler Co., Inc.
0
Comments
-
Max. air pressure test on old Burnham cast-iron baseboards?
What is rated maximum pressure that can be safely applied to older Burnham cast iron baseboards? I need to pressurize a few zones one at a time with air pressure to find which heating loop has a slow leaker. I don't want to risk damaging anything. The boiler will be off the loops during the tests.
Pete0 -
I think its 50 psi
But Glenn Stanton can answer this for sure.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 103 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 936 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements