Steam vs hot water
Jim Roberts
Member Posts: 1
I am working with a 2.1 million low pressure steam boiler, it's output is 1.6MBH.. I was thinking of staging three 550MBH output boilers; question is this a smart move.. I know it is not like staging hot water boilers where the temperature is increased as needed, however steam is steam...help please......
0
Comments
-
The cost vs. benefit
of such a design is suspect. We have done a few "modular" steamers and as you might suspect, the three boilers run to get up a head of steam - then one or two drop out to maintain low pressure of ~ 1 PSI. The condensate feed issues become a nightmare and three receivers vs. one as well as the controls to make it work become hairy.
Having a 2.1 million (written as MMBTU, not MBTU as you wrote [for the output] @ 1.6 (sic) MBTU) suggests a power burner may be the boiler's burner design? It's much more effective to simply install a modulating burner. If atmospheric - easier to stage the combustion racks - than change to a new boiler system/design.
If on the other hand, the existing system is toast, I would opt for a single boiler with modulating burner. Easy to get what you want at a far better price and easy, straight-forward boiler feed options.
Before doing any design work, please check the amount of standing radiation to get a load number. Never size a replacement based on what's there. Always measure and calculate EDR based on existing radiation.
Let us know how you make out.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Mod vs. Lead/lag
The previous post on modulation has merit if the gun/boiler is reasonably efficient over the range. With modulation you eliminate the pre and post purge losses and long off times. Multiple units with lead/lag control headaches and flooding of the off units; something that can only be reduced not eliminated by header design. I have done both (more mods then lead/lag) and would certainly explore the modulation first.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements