Erik_4 Member Posts: 2
I am having trouble getting one stage of a six stage boiler system to work. I am having troubles with stage 3. Stage 3 and 4 are wired together off of the same 24V transformer, stage 4 operates fine, but stage 3's burner is not lighting when it is called for by my control. Both stage 3 and for again are wired together off of the same transformer. I am getting the correct voltage at the gas valve on stage four, but when I test stage three, I am getting no Voltage. So in my mind that would mean I have no return voltage to the transformer. But I just don't understand how stage 4 works correctly and stage three doesn't light at all. Any have any troubleshooting or solutions for me. thanx
  • What kind of
    system is this, make, model, gas valve numbers, control numbers. Are you a service tech? If not I suggest you call a professional.
    What is your location?
  • Erik_4
    it is a forced hot water system. Yes I am a Service Tech. I am useing a Tekmar Control, Not sure of the numbers on the Honeywell gas valve, since I left the boxes at the job. I am in boston. They are a series of Cast Iron Boilers. They have just simple aquastats on the boilers, and the Tekmar tells the stages to fire according to outside temperature.
  • Todd_17
    Todd_17 Member Posts: 31
    I'm sure
    I am sure you checked for proper connections, i am asuming parallel, but check the integrity of the connections for corrosion. under load of gas valve the connection might be compromised
  • Mitch_4
    Mitch_4 Member Posts: 955
    seems to me
    that if you have 24v feeding the wire to the valve, but no 24v at the other end, check the continuity of the wire....