Weil Mclain Ultra gas Condensing Boiler

I'm located in Kingsford. Wholesale sales. We have a branch in Marquette.

Comments

  • mike faust
    mike faust Member Posts: 58
    Has Anyone used this boiler? Any feedback?

    We will be installing a Weil McLain Ultra gas boiler in a replacement application in a few weeks. The existing system is cast iron radiation in one zone and an aluminum finned baseboard series loop as the other zone. Though I've installed other condensing boilers, this is my first time using the "ultra." Anyone know of any special considerations with this product???
  • Glenn Sossin_2
    Glenn Sossin_2 Member Posts: 592
    Install as per the manual

    and leave it off the wall a few inches so you can get to the electrical terminal strip after you've got the exhaust and intake pipes connected.
  • Yooper Rick
    Yooper Rick Member Posts: 22
    Ultra

    Also, make sure to use a dirt trap or wye strainer on the return to catch anything from the cast iron radiators.
  • mike faust
    mike faust Member Posts: 58
    strainer

    Good point! They should suggest that in the install instructions....
  • Shane_2
    Shane_2 Member Posts: 198


    I have put in a few Ultras, including my own home. If possible do your wiring first, even before the venting, it's a little tricky wiring around the vent pipes. Follow the instructions exactly(primary/secondary etc.) I would be careful with a wye strainer due to the flow restriction you will already have getting through the heat exchanger. If you can find a dirt seperator for your application, that would be my choice. I couldn't find one smaller than 2" for a small cast iron/mod-con job I did recently.
  • ALH_4
    ALH_4 Member Posts: 1,790
    Dirtcal

    How about the Caleffi Dirtcal?
  • Shane_2
    Shane_2 Member Posts: 198
    Slightly off topic

    That is exactly what I was looking for. I went to five of my local suppliers. They all told me the Caleffi or the similar Spirovent, or even B&G versions were not available form their distibuters.
  • Tony_23
    Tony_23 Member Posts: 1,033
    Wye strainer

    You'd install it in the system loop, not the boiler loop. I don't think a wye strainer has much head resistance besides. As long as minimum flow thru the boiler is maintained, everything's good :)
  • Ross_7
    Ross_7 Member Posts: 577
    Where you at?

    Rick, where are you located? I'm in Marquette
  • Tombig_2
    Tombig_2 Member Posts: 231
    Ultra boiler

    As others mention, do your wiring before the final PVC work, especially if you're wall mounting. The wall hung kit is not shipped with the unit BTW. Back up wrench the S&R piping as the compression connections to the aluminum boiler block are rather tenuous. Use a strainer or seperator on the return. Increase to recommended primary loop size ASAP after factory 1" nipples. Wire brush, tape, dope to factory nips as there's usually a little corrosion on the threads left over from the hydrostatic test at the factory. The OD reset curve comes factory set to flatten out at 32*F. Instructions to customize the curve might be in the new I&O manual. If not it's available from W-M. Download or view the I&O and vent supplement from their website before delivery so you have no surprises at delivery. W-M has an extensive downloadable library. Good luck.

    Tom G
  • mike faust
    mike faust Member Posts: 58
    Thanks Andrew

    Thanks... Gonna order one as my distributor does not carry.
  • Ross_7
    Ross_7 Member Posts: 577
    You mean Wittock's Supply?

    Is this Rick Bath?
  • Yooper Rick
    Yooper Rick Member Posts: 22
    Ross

    Yes & Yes. Wittock Supply-heating sales.
  • Buzz G.
    Buzz G. Member Posts: 61


    Dirtcal, where did you order it from?