Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Pressure
Pedro
Member Posts: 1
How can I tell if the boiler is currently working at the settings of the pressure trol that is set?
I have a pressure guage but it reads in lbs and wont be effective.
I have a pressure guage but it reads in lbs and wont be effective.
0
Comments
-
You will need a pressure gauge of
the appropriate scale, Pedro. McMaster-Carr has them in ounces if you like, available on-line. I have already ordered some from Winters before I got word about M-C, but they have not arrived yet.
The gauge you have on the boiler is a code requirement, not particularly useful as an instrument, just a safety device.
A gauge reading 0-5 PSI should be fine with a pressuretrol and if you are using a vaporstat, 0-32 ounces (0-2.0 PSI) would be better."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
Thanks to you senor Brad.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements