Fancoil pressure drop

BC_3
Member Posts: 12
Maybe the flow meter itself has a significant pressure drop? the pressure drp through some meters is huge as they approach max flow. They should have data on this. Maybe the spring check, although I wouldn't think that would contribute much.
0
Comments
-
Pressure drop -- fancoil system
I have an ESP HE-50 hot water fancoil connected to a standard 75 gallon direct vent tank type water heater.
The mfgr calls for 5GPM through the fancoil which is 1/2" copper. Literature states that there is 5ft/hd drop through the fancoil. The rest of the piping is about 20' of 3/4" copper to and from the tank. 1 spring check. With a Grundfos 15-42 pump on high I am getting only 2.5GPM through the loop!
The pump curve of this unit tells me that at 2.5GPM I have about 16 ft/hd. Where is all this resistance coming from?
The two items I have considered are:
1) Because of space considerations I do not have 5 straight inches before and after the pump. The pump is just after a 90° elbow out of the fancoil. Does it matter that much?
2) I have returned the fancoil to the cold water inlet (dip tube) of the water heater. Is there that much resistance through the tank? Would it matter if I returned it to the drain fitting at the bottom of the tank where the hot water re-circ is located?
I'm pleased I put a flowmeter on the system to see what is really going on, but am suprised that I would need so much pump to get my flow rate.
Who's got insight on this one?
Thanks,
Jacob0 -
flow rate
I wonder if your flow meter is right. Was is the delta T of air side. What about checking your actual pressure drop across fan coil. either one of these can tell you what actual flow rate is. Tim0 -
Flow Meter
The flow meter itself is very accurate. A blue white graduated cylinder type. However it IS installed right after the pump where there may not be good laminar flow.
I do not have the ductwork connected yet so I do not have the delta T of the water in and out.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements