Steam radiator vents

Dave Stroman
Member Posts: 765
I would like to start using Gorton steam vents. For those of you who are familar with them, you know that they make a #4, #5, #6, C, and a D. Each with an increasing amount of air being vented. But they also a model #1965. They do cost less and I would like to know how they are different from the others.
Dave Stroman, Denver
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=506&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Dave Stroman, Denver
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=506&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
There was an error rendering this rich post.
0
Comments
-
I believe
the 1965 lacks a float. Spend the extra money.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thanks Steamhead. I did just get off the phone with Ken at Gorton. He helped a lot. Do you use the Gorton radiator valves? Which one do you use the most, or do you use them all? I am ordering some from a place I found on line as we have no local suppliers. Probably will order some of the C's and a couple of the #2's.
Dave Stroman, Denver
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
You'll use lots of Gorton #2 main vents
especially if you calc vent sizings by Gerry Gill & Steve Pajek's charts. We just ordered our second dozen #2 vents this fall, and will likely burn thru those rather quickly.
For radiators, I use the Gorton #4 on the very smallest ones. Next sizes up are the Hoffman #40, then the Gorton #5, and for the largest rads the Gorton #6. A wide-open Hoffman, Vent-Rite or Dole adjustable vent roughly equals the #6. In some cases we need to go larger, using a Gorton C or D, but that's rare if the mains are properly vented.
If the user wants to be able to vary the heat in a particular room but doesn't want TRVs, the Vent-Rite #1 is a good choice as it can be adjusted without tools, even shut off completely. It's best to use a Vaporstat with this setup, higher pressures will cram more steam into the rads by compressing the air.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements