burnt up or fried 24 volt transformers

geno54
Member Posts: 40
In the future when troubleshooting, a low amperage inline circuit breaker or 3 amp fuse ( automotive style )will help save many a transformer. Just a tip
0
Comments
-
24 volt transformers
ok guys put on your thinking caps we installed a new boiler (gas) steam 3 weeks ago we have replaced 4 24volt transformers we had an electraicain in if we disconnect the water feeder(on the 24 vt. system)it works ok tryied a new feeder thought the first one was faulty fried another one so what could be doing this we are all baffled we checked all we can check and r stumped what are we overlooking guys?? burnerman/royboy0 -
Check the specs on the transformer and the water feeder
Some of those 24V water feeders take 40 watts, and some of those 24V transformers are only good to 20 watts. It's probably not a short becuase you'd smell that right away.
Make sure your transformer is rated for the water feeder load.
0 -
I buy
control transformers with built in circuit breakers. It's a lot easier resetting a button than rewiring a new transformer every time there's a problem. Gives you more chances when troubleshooting too. The brand my supply house uses is Jard. Just look for a CB at the end of the model number on the box that indicates circuit breaker. WW
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Too much load
You'll need either a higher capacity t-former or a seperate one for the feeder.0 -
Jard good
Also; Honeywell AT 150/1750 -
Save the transformers
a couple of 1/4" spade connectors a 3 amp fuse and a little black tape has saved many a transformer J.Lockard0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements