Anything wrong with this install?

If the windows remained closed, wouldn't the glass block the UV?

Alex
"Let me control you"

Lost in SOHO NYC and Balmy Whites Valley PA

Comments

  • Dan Sedens
    Dan Sedens Member Posts: 48
    New Munchkin M80 install with Vision 1 pics

    Please pick it apart so I can do better next time. I can't seem to get enough out of this site. All scrutiny is more than welcome. Thank you.
    Dan Sedens
  • The Wire Nut
    The Wire Nut Member Posts: 422
    I'm no expert,

    but focused photos would sure help...

    Alex
    "Let me control you"

    Lost in SOHO NYC and Balmy Whites Valley PA
  • ScottMP
    ScottMP Member Posts: 5,882
    I'd invest

    in a new camara :) Really i looks O.K. but its really hard to tell from the pictures.

    The fact that you care and came here says alot.

    Scott

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Ben J
    Ben J Member Posts: 2
    install pics

    pex tubing can be deteriorated by uv light, tubing in front of window is a bad idea
  • Ted_9
    Ted_9 Member Posts: 1,718
    Install

    Seems ok but the pics are out of focus and too dark.

    Looks like you care about your installs though.

    What did you get for combustion numbers on start up.
  • Alex \"The Wire Nut\" Marx.

    Nope.

    Dave
  • Larry Savino
    Larry Savino Member Posts: 63


    Well I cant see the near boiler piping to tell if its a good circut or how the circuts actually run? I just cant tell from the pictures the mecanics of it.

    But I think it looks outstanding,Everything neat and orderly,look well planned out and ordery for future repairs or maintnence or adjustments. Great job I wish I had the paitence to preform work like that. I just completed a munchkin in my own home and am imbaressed to post the pictures of the complete work. Last thing you should know that what ever quaility heating guy goes behind you in that home will be saying for the next couple of decades WOW a quility craftman installed this system


  • Check me, but I believe a window of clear Lexan (GE tradename for polycarbonate) will block UV.
  • Steve

    Perhaps, IF it`s that type.
    How did we get talking about this anyway???

    Dave


  • Is it piped P/S? It looks the radiant is, but the DHW is not?
  • Dan Sedens
    Dan Sedens Member Posts: 48


    Sorry about the photos. Either I had too much coffee or my camera sucks. I'll go with the later. Thanks for the input. The U.V Issue didn't even cross my mind. Would it be fine if I put armoflex on the risers? I thought I should have done copper on the risers, but in the interest of saving time... Decided to go with pex instead.
    Thanks
    Dan
    Sedens Plumbing and Heating, Inc.
  • Dan Sedens
    Dan Sedens Member Posts: 48
    Fitty

    The radiant is piped P/S. The DHW comes off the primary loop as the manufacturers specs show. I think this has to do with temp./head pressure. Don't really know for sure. I basically went directly from manufacturers drawing as this is my first install of this type.
    Thanks
    Dan
    Sedens Plumbing and Heating, Inc.
  • Dan Sedens
    Dan Sedens Member Posts: 48
    Ted

    Out of the box, Because I haven't been able to get back to ajust I got...
    138.2 Stack Temp.
    9.35% CO2
    89.2% Eff.
    22.4% EX Air
    4.2% Oxy
    31PPM CO

    Thats on low fire.
    On high Fire, I got..
    149.6 Stack Temp.
    6.73% CO2
    88.4% Eff.
    65.8% EX Air
    82PPM CO