Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Buderus Wall Hung- circ / vlaves
Louis_5
Member Posts: 1
Hello and thanks for the very informative site. Priceless!
I have installed a new heating system in my house; 3 zones high-output fin-tube BB and sized it at 150 F at 10 F outdoor temp, central New Jersey, (had to make it look nice too- tried to get it to 140 F but just didn't have the space for more BB), 3- 200' loops with 3/4" pex and am considering zone valves? I think i decided on the GB142- questions:
1. which circulator should i install for the zone valves? or should i use circ for each zone? trying to make it the most efficient.
2. As it is glycol, how do i figure the quantity of water in my system to calc. the glycol mix? how much water in each foot of 3/4 pex?
3. do i need to use a header?
4. any other suggestions or ideas would be great.
thanks
I have installed a new heating system in my house; 3 zones high-output fin-tube BB and sized it at 150 F at 10 F outdoor temp, central New Jersey, (had to make it look nice too- tried to get it to 140 F but just didn't have the space for more BB), 3- 200' loops with 3/4" pex and am considering zone valves? I think i decided on the GB142- questions:
1. which circulator should i install for the zone valves? or should i use circ for each zone? trying to make it the most efficient.
2. As it is glycol, how do i figure the quantity of water in my system to calc. the glycol mix? how much water in each foot of 3/4 pex?
3. do i need to use a header?
4. any other suggestions or ideas would be great.
thanks
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements