CALCULATING CIRC HEAD LOSS
BRIA SCHWARTZ
Member Posts: 1
wHAT IS THE BEST WAY TO CALCULATE THE HEAD LOSS FOR PROPER CIRCULATOR SIZING ON A BRAZED PLATE HEAT EXCHANGER THAT IS PIPED IN ON THE RETURN OF AN OIL STEAM BOILER?
THANKS
BRIAN
THANKS
BRIAN
0
Comments
-
Brian,
Step #1. Get any kind of reference pressure drop through this heat exchanger. Any reference to a pressure drop. (something like (2 gpm @ 1# or 2 gpm @ 2.31')
Step #2. Do you know what the gpm that is required? If not, what is the btu's you want to transfer?
Step #3. I use my B&G System Syzer to "figure" the new pressure drop required with "your" gpm. (I can do that if you give me the information from step 1 &2)
Step #4 Keep in mind this is only for the heat exchanger and not for any piping loss.
Peace.
bobbyg
0 -
If this is an old existing heat exchanger, just give me more information....What is the heat exchanger for? What is their now? Pipe size, existing pump, etc.
Give me something to work with and we can figure it out.
What is the situation....homeowner, contractor, etc. Doesn't matter, just need to know how detailed to get.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements