Radiant Floor manifold placement!
Arrived at a new customer with 2 year old radiant floor install.First thing I saw in the basement was all 4 manifolds are below the tubing. Air elimination is done by purging and boiler is piped with a 1 1/4" spirovent. House is well supply with a variable speed submersible pump. It is impossible to get all the air out with the manifold and its placement. The house is 16,500 sq. ft. but not total radiant. I need help in documentation and try to explain for relocating, after the man just spent $5M in construction. Thank You
0
Comments
-
Manifold location
should not be an issue. It sounds like the system does not have a good way to isolate zones to power purge. I suspect a lot of tube and volume in a system that size. I doubt you could purge all the lines at once with a 1/2" feed at 12 psi setting.
Once you get flow in all the loops the air purger will handle the small details. It may take hours or a day to get all the small bubbles out IF you have flow in every loop and zone.
I like to valve every manifold and install a full port purge valve like the Webstone. It can be done at the boiler room often if all the manifolds are piped to that room. It takes a bit of time to purge a large radiant system, even with correctly placed purge points.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Purging
You should be able to purge the air out of each loop using the manifolds shut off valves ....What problem have you found ?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements