How can I tell if the mains are venting quick enough?
I have a one pipe steam system, and currently have a Gorton #1 at the end of each main.

Comments

  • timing

    When the mains are cold, turn up the heat and time it's movement. Start your stopwatch when the header above the boiler gets steam-hot. Go to the main vent in question and stop your stopwatch when the vent gets steam-hot.

    In general, a good time is between one and two minutes for the main to fill with steam.

    Noel
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    Tell us

    the length and diameter of your mains, and we'll let you know. Then time them out like Noel says.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Irv
    Irv Member Posts: 95


    One of the mains is 49'
    The other is 33'
    The diameter of the pipe is 2" (outside dimension 7.5").
    I currently have one gorton #1 at the end of each main, and am considering adding others off a tree.It is one pipe system.