International Mechanical Code & Hydronic Tees
Dave E.
Member Posts: 9
I think I must be misunderstanding this, or else it seems to outlaw diverter tees. I suppose the branch opening must be the middle opening. But then, the illustrations I've seen of the main riser from a boiler connected to the middle opening of a tee, one side to a boiler drain and the other supplying the radiation, seem to be against this code. So I still don't know what's up.
0
Comments
-
Code Limitation on Tees
While tinkering with my water boiler hydronic piping and reading my 2003 International Residential Code (which consists of sections of other International codes) I ran accross:
"M2101.7 Prohibited tee applications.Fluid in the supply side of a hydronic system shall not enter a tee fitting through the branch opening."
Does anyone know the reason for this? I thought it would be a good way to put a gauge in the line if I ran the supply through the branch openings and used the middle opening for the gauge.0 -
I think this means bullheading a tee on the supply is outlawed. "shall not enter a tee through the branch"0 -
That's a prohibition against attempting to equally split flow via supply through the branch of a tee. The "middle" opening is the branch and such is perfectly suited for mounting a gauge.0 -
NO BULL...
headed tee's allowed.
Exceptions include primary secondary applications, variable speed injection applications, and diverted prioritized flow considerations.
I attempted to write a clarification to the IMC regarding this statement, only to be told that all references to it were yanked in the new code.
Guess the enforcers couldn't interpret it either :-)
ME0 -
Section 1206.1.1
If your IMC has figure 1206.1.1 on the next page, as others have posted it is perfectly code compliant to install a gauge in the branch (bull) connection. The figure will make you aware as to this sections meaning.
1206.1.1 shows both an acceptable tee and a prohibited bull-head tee arrangement. Installation of bullhead connections creates excessive pressure drop, flow resistance and poor system perormance. The intent is to prevent supply-side fluid flow from entering the side (branch) opening of a tee when that opening connects to a main, and the straight-through (run) opening of the tee are used as branch connections flowing in opposite directions.
Hope this helps!
Robert O'Connor/NJ0 -
Thanks, I'm using the International Residential Code for One- and Two-Family Dwellings, which omits figure 1206.1.1
Now I know.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements