Supended in Concrete or stapled to foam

Dirty
Dirty Member Posts: 7
Does any one have performance data on either. The designer is questioning the performance of tube stapled to the foam. He also belives its makes the concrete weaker. I need to set him straight. Any help would be appreciated.

Comments

  • hot_rod
    hot_rod Member Posts: 23,398
    Ideally

    the tube would be placed about mid slab. Siggy has written several articles on the performance difference based on tube depth. Find them at www.pmmag.com may 2000 column. His model shows about a 30% difference between the tube at the bottom of a 4" slab, and 1.7" below the top surface. water temperature adjustments need to be made to equal the btu/ sq ft. output.

    I will say suspending the tube exactly in the ideal location is easier said than done. i've used mesh and chairs as close a 3' on center and still get droops between them.

    Caution needs to be taken when pumping concrete over elevated pex. the force of the mud flying down the tube has a tendenacy to float it to or through the top surface. It also leaves the tube vunerable to saw cut expansion control joints commonly used these days.

    I'm not following the logic of how the tube could make the concrete weaker?

    Adding water to concrete at the job site weakens the mix considerably. Every gallon of water added to a yard proper concrete mix reduces the psi rating by 200 lbs.

    Lazy concrete finishers often add 8-10 gallons to get the mix to flow into place with the least amount of effort.

    hot rod
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream