Steam boiler trim.

Dave Stroman
Dave Stroman Member Posts: 766
The last steam boiler I replaced I used the McDoonald-Miller #67 low water cut off with a #101A feeder. It worked just fine. But I see a lot of # 47's around too. Any thoughts on which is a better one to use on a small 125,000 Btu gas fired boiler? The last boiler I used was a Peerless. Again, it worked fine but maybe a little pricey.

Ok, check my numbers- Connected load is 219 sq. ft. Multiply by 1.5 pick up factor and multiply by 240 to get the total Btu's needed of 79000. At this altitude I divide by .67 to get my input Btu's. That accounts for a boiler that is about 84% efficient and about 20% for my altitude of 5280. I come up with a boiler needed of 118,000 Btu's. Is there anything I am missing?

Dave Stroman, Denver