munchkin outdoor reset
you would need to set the minimum temp on the reset curve to remain high enough to trigger the air coils.
and, unless you're doing high temp radiant, you need to mix down from the high temp zones for the radiant. That means either vision two, or additional third party controls typically.
and, unless you're doing high temp radiant, you need to mix down from the high temp zones for the radiant. That means either vision two, or additional third party controls typically.
0
Comments
-
munchkin 199 w/ outdoor reset
Hi I have a 199k btu munchkin boiler. it is used for four high temp zones with hot air coils and 4 zones of radiant (ceramic tile). Will the outdoor reset in the vision one kit lower the outlet temp., or will it produce a high temp setting and just modulate to keep producing the high temp.
If it lowers the outlet temp w/ relation to the reset curve, how can I use it with the strap on aquastats for the blowers. Any help is appreciated.
Thanks0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements