I'm currently installing an Argo AT using the Argo AZ-4P control. It's a replacement for a small house and the HO wants to use the two existing zone valves. I don't have much experience with zone valves but I said ok and bought the AZ-4P. The existing zone valves are Honeywell V8043F models. I would like a little verification of the terminal wiring. Argo control zone 1 has terminals T-T for stat and terminals 1 2 3 4 for zone valve. The Honeywell zone valve has five terminals, TH-TR , TH , TR , and end switch. I guess I'm just not getting it.
0
Comments
-
Zone Valves
Do the zone valves have colored leads coming off them???
The Yellow & Orange are power to the motor, the 2 Red are the end switch. Does this help?0 -
The end switch
terminals go to 3&4. The valve opens when power is applied to Tr & Th,so 1&2 go there.The Tr-Th terminal is just a junction to send power to T-stat when using a standard transformer and not a zone panel.Take a look at the underside of the terminal board and you'll see the Tr-Th is not wired internally
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
TH-TR
Thanks Robert.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements