Steam boiler riser location
David Nadle
Member Posts: 624
"The Lost Art of Steam Heating," sold here, will be worth every penny to you. Read it before you start installing.
0
Comments
-
Steam Boiler Riser location
I am replacing an old Bryant boiler, which has a single supply riser out the top of the unit with a Utica unit which has a supply out each side. So the recommend piping is to come out each side, rise and connect across the boiler. The riser to the house system would then tee off one side. It would be more convient to place the tee between the two feeds from either side of the boiler so that the connection is centered above the boiler, but I didn't know if that would affect the performance. The several installation manuals I've looked at for steam boilers all show the riser between the boiler suppy and the equalizing loop. What do you think?0 -
You were smart to notice
that the manuals showed the takeoff after the risers; the manuals have it right. You don't want the house riser between feeds because you want all the steam travelling in the same direction, not colliding at the tee.
Also, there should be a slight slope down to the equalizer after the supply risers join. You want the return condensate from the not-yet hot supply pipes coming back down the house riser and going into the equalizer, not backsliding down the supply riser like it would if it were on the wrong side of the slope down to the equalizer.0 -
Mike, here's a pic
of what the piping should look like on this type of boiler.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements