Sizing 2 pipe steam systems
Options
Unknown
Member
Just the radiation, and the piping and pick-up factor that is built into the steam output ratings on most manufacturers literature (so that you don't need to add it in).
Unless it is an old 2-pipe air vent (or Paul System), there are likely metering devices (special valves; OR orifices) on the inlet to each radiator, and these limited the steam volume to LESS than the radiators could condense.
Size to the radiators.
Noel
Unless it is an old 2-pipe air vent (or Paul System), there are likely metering devices (special valves; OR orifices) on the inlet to each radiator, and these limited the steam volume to LESS than the radiators could condense.
Size to the radiators.
Noel
0
Comments
-
Sizing 2 pipe steam systems
Does one take into account the return piping when there are no steam traps present . This is an old system where the return piping from each radiator drops into the condensate return located in basement . I'm trying to size this boiler properly . Any help would be appreciated.
Bob0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements