pressuretrol & short cycling
Options
ronnie_3
Member Posts: 4
Does lowering the pressure in the system, cause the boiler to short cycle more? Would it turn on/off more at 1.5 vs 2.0 lbs, if the system didn't yet reach the set temp of the thermostat?
Thanks,
Irv
Thanks,
Irv
0
Comments
-
If
the system reaches pressure setpoint prior to getting steam to the radiators (or the mains, let alone the radiators), I would check the venting first.
Too little venting will back-pressure above setpoint, especially one so low."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0