Quirky Steam balancing problem

next thing to check for is marginal pitch on the slow steam main. Maybe there's a water pocket forming somewhere- look for a broken pipe hanger.

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Tom Hopkins
    Tom Hopkins Member Posts: 554
    Quirky Steam balancing problem

    I have a one pipe steam system with the following dimensions:

    Left side main 49' X 2 1/2"
    Right side main 45' X 2 1/2"

    The left side has a connected EDR of 192 and the right side is 98 EDR.

    Both mains are well insulated. The left side is vented with one Gorton #2 and two Hoffman 175s. The right side is vented with one Gorton #2. The problem is that the left side vents much slower than the right even though is has much more venting. Also, the rad at the end of the main on the left side gets very little (if any) steam and it's closest to the t-stat.

    I have enclosed a drawing of the system.

    Notice that there are three large rads on the left side which are close to the boiler and I wonder if they're stealing steam?

    Do I need more venting on the left side to balance with the right side?
    I have not been able to find a pro in my area that has been able to help.



    Also, there are two plugs in the mid part of the left side main. Could I put
    another vent in one of these to quicken the venting?

    Any suggestions would be appreciated.
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    That behavior doesn't make sense

    there has to be a problem somewhere.

    How about posting a pic of the near-boiler piping?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Jeff_100
    Jeff_100 Member Posts: 1
    Here's a pic

    We had the boiler replaced last year. The old one was a very large Weil McClain. The new one is MUCH smaller. I had them install a dropped header.
    Even with the old boiler, the balancing problem was the same. I did find
    that some of the large upstairs rads. had lost their insulation on the risers. I opened the floor and dropped insulation into the wall chambers that house
    the risers. Now the floors in those areas don't get hot and the heat stays in the pipes.

    Any thoughts?
  • Phil_17
    Phil_17 Member Posts: 178
    Are the two mains fed from separate risers

    My old system (recently replaced) had a setup where the boiler had two tappings, and each one was directly connected to my mains (no header connecting them, no equalizer, and no hartford loop either: check valve). One of the mains just never got good steam. The other would heat quickly and quietly but the "bad" one acted much like what you are talking about.

    When we replaced the boiler a couple months ago, the guys put in a new MST with proper header, equalizer, and hartford loop... The cold main heats like a champ now, and I actually have been able to get some balance in the venting. This piping stuff really does work like Dan's book says it should :-)
  • gerry gill
    gerry gill Member Posts: 3,078
    you may have

    the closer radiators stealing steam, just as you think..we call that runout robbery when the runouts and radiators steal the steam from the main before it gets to the end.. test this by closing the closer radiators and seeing what happens..if it works better, put tiny vents on those radiators and big vents on the far end.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Tom Hopkins
    Tom Hopkins Member Posts: 554


    The pitch in the mains seems correct - no broken staps. I took Gerry Gill's suggestion and shut off the biggest rad (42 edr) and the rad at the end came
    right up to full heat and steam got the end of both mains at about the same
    time. The vent on this big rad is not adustable...I wonder if I should get an
    adjustable vent and set it at its lowest setting?

  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    If someone put a big vent

    on that rad in an attempt to make it heat faster before the main vents were upgraded, that might be causing the problem now. What vent is on that rad?

    Try an adjustable vent like a Hoffman #1A, this will let you fine-tune it.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Tom Hopkins
    Tom Hopkins Member Posts: 554


    Currently there is a Maid - o - mist non adjustable vent (#6 I think). I'll try
    the adjustable and set it low.

    Thanks