Sulphur smell!?
Al_19
Member Posts: 170
If the odor is ONLY in the HOT water, then you probably have a tank type water heater with a magnesium anode rod. You would need to replace the magnesium rod with an aluminum/zinc rod, and disinfect the tank and hot water piping with hydrogen peroxide.
If the odor is in both the cold and hot water, then it needs to be adressed from the well.
If the odor is in both the cold and hot water, then it needs to be adressed from the well.
0
Comments
-
?
We have a client in Jermyn, PA that we just finished a vacation home for and they say that when they use the hot water, there's a terrible sulphur smell!? The home's water is from a well. Being from North Jersey where all the homes we do are on city water, I'm a little stumped. Any explanations? Any solutions?
Thanks in advance, Adam0 -
!
The house, water heater and plumbing are brand spanking new. Why would a magnesium rod cause the smell?0 -
Fowl smell and taste
Doesn't matter at least in my duplex changed water heaters and less than 3 months had to get rid of the rods and went with the aluminum/zinc style. Back to normal in less than a week.0 -
Divibrio Sulfurcans ??
See attachments0 -
Comes....
with the territory in the Northshore area of Milwaukee, we have encountered this problem numerous times.Unfortunately the last one was not completely solved using your technique(s) Glenn.
It starts with the source water and is amplified by the warming of the water. Makes sense that water expands when heated so the sulphur smell would be more evident after the heat process.
Seems to me that Glenn Schlueter (State of Wisconsin Water Specialist) addressed this problem at one of his informative seminars. I will research his and see if something can be done with the source water prior to household use.
R. Kontny
Make Peace our Passion while supporting our Troops!0 -
www.smellywater.com
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Nothing like a good rotten egg
In NE Indiana if its in the country the rod comes out, if the city no. Yes it voids the warr, but the mfgs. know it happens and dont ask for the tank back. My wholesaler just started to stock heaters with alum. rods so no longer necessary.0 -
Rotten Egg Smell
Finally had a minute to research the rotten egg smell with "The State of Wisconsin, DNR website"
If you go to that site and look up private water wells you will find a section on different water contaminants.There you will find a 4 page pamphlet (that is printable) that explains the problem and gives solutions.
As posted it starts with sulfur bacteria that is a very common element in nature, it occurs naturally in some aquifers.Sometimes it is caused by the well drilling techniques and this is a likely suspect in this case.
Whether it is naturally occuring or part of the well drilling process makes little difference as far as solving this problem goes.Shock chlorination of the well with chlorine can treat the well but should be done with proper care and techniques.
As far as the water heater goes you don't necessarily have to remove the anode. Especially with a new home! Instead make sure your heater has a properly sized and maintained relief valve and then increase your water temperature to a temporary setting of 160 dergrees for about 8 hours. This temp. will kill off the SRBs. Remember to warn users of the higher temp and make sure you turn it back down to the safe levels after the treatment!!!
I can e-mail this to interested parties or they can look up the site.
Rich K.
Make Peace Our Passion while Supporting our Troops!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements