Probe-type LWCO question.
kevin coppinger_4
Member Posts: 2,124
a set of alligator clips?
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Hi, everyone.
I'm trying to fool a probe type LWCO into working while mounted on a wooden board as part of a complete burner circuit.
I thought I would just have to ground the probe to the control's casing.
That doesn't seem to be the case.
Any ideas?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Is the idea to
get it to make or break, John? I would think you would have trouble getting it to "make" without water.
Would inserting it into a tube you fill with water and have a base drain valve work?
Sounds like a nice demo board you are preparing but that is just my guess. Sorry of not much help."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
You guessed it, Brad.
I could conceivably screw a tube of water onto the probe but I feel like I shouldn't have to do that.
A circuit is a circuit, no?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
A circuit is a circus....
In principle, yes, but the probe types I have seen have a shielded probe inside the sheath and the protruding one into the pipe. The internal contactor is isolated from the sheath so you would have to get into the works to make a connection.
They are designed this way to minimize shorting out the circuit (keeping the boiler operating without water) if contact is inadvertently made.
I think what you are trying to do is defeat this feature for the purposes of demonstration. As to how that would be done without water? I will shut up now. I have no idea."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
I'd say,,,
rig yourself a small tank to mount the probe into and fill with water, then you can drain the water in some fashion and the students can watch as the level goes below the probe and the "boiler" shuts down on LWCO.0 -
Yeah...
...I tried that.
What should I be clipping to?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
A direct short...
A direct short won't work, that would simulate the probe grounding against the pipe it is screwed into... Think about a resistor between the probe and ground to simulate the conductivity of water, not steel! The rating of the resistor, I have no idea, they are cheap thru Radio Shack, you may also find a multi pack there. Keep trying different values till the LWCO makes. I hate to recommend them but there really is no other place to put your hands on small electronic components.0 -
Probe LWCO
Just had 2 MM probe cutoffs where water was such that it said we had a shorted probe. MM tech help told me to replace lead to probe with 100 ohm 1/2 watt resister, fixed it. I dont know if that would work on the other end or not.0 -
Ahh-HAAAA!
That sounds like the answer.
Just one question: I should put the resistor between the end of the probe and...what?....the 3/4" threads?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Well done.
PLUMBARIS and Brian K:
The 100 ohm, 1/2 watt resistor worked like a charm.
Learning stuff every day.
Thank you both VERY MUCH.
Hope to see you(s) at a Big Ugly soon.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Big Ugly
not a term I've heard before other than a referance to a few of my clients, what is it0 -
It's a thing....
...where everyone gets even more more stupider than usual.
Haha.
It's just a get-together of people that participate here usually involving much food and drink.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Glad to help...
No problem... I was slated to go to the MA seminar and Big Ugly but work got in the way! It was held not 5 minutes from my house. I'm looking forward to putting faces to names at the next one.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements