Taco flow checks
targetman
Member Posts: 105
Can I use Taco flow checks with zone valves?
0
Comments
-
Yes.
But only if required. Each fitting of that ilk adds resistence to flow to a zone - thereby reducing flow slightly.
Given that ZV's are already positive checks, why add yet another? What are you trying to overcome?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
The job was originally circulators.0 -
remove
Remove the flow checks, they are not needed.0