weil mclain wiring
Michael J. Brennan
Member Posts: 29
Hey Carol, was wondering if you could answer a couple of questions for me, i am going to install a weil mclain ultra 80 boiler along with a weil mclain indirect fired water heater, and 4 baseboard zones, i am going to use a weil mclain wmcr-6 circulator zone controller with prioity, i was wondering if i should wire the indirect heater to the zone controller as priority, or wire the indirect heater to the control board on the boiler. Also would you know where i would have to land the wires from the circulator zone controller to the boiler control? thanks for imput....
0
Comments
-
The Weil-Mclain Ultra tank will only wire to the boiler. It actually uses a resistor in the tank to fire the boiler. Also the boiler has efficiency algorithms built in to the unit.
Additionally you will most likely want to use the outdoor reset feature which will change the supply temp to your heating system based on outdoor conditions. This will give you the best efficiency then when the indirect needs heat it ramps up the heat to the water heater only.0 -
Just a thought
Don't forget to pipe Primary/Secondary.....
Mike T.0 -
Wiring an Ultra
The indirect should be wired to the boiler's terminal strip, just as Josh stated.
The other wiring connection locations are pointed out in a book called The Installation Manual. It's a good idea to use it...0 -
Priority
will be provided by the MCBA board when it sees a demand across the DHW terminals. It will also bypass the ODR curve this way and ramp up the boiler to the DHW setting what ever you have it at.
Good luck
Glenn0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements