pressure loss with spring check valve
Options
Tom Noftle
Member Posts: 16
Hot Rod thanks for responding. I'm using an on demand water heater for DHW and for a loop to a HX to heat my floor. I'm a carpenter not a boilermaker so these cv factors and pump curves make my head spin. I'll see if I can find the info you refer to, but, I'm not sure I'll know what to do with it once I have it.
Tom
Tom
0
Comments
-
how much will a spring check valve restrict the flow on a loop going to a flat plate heat exchanger? will a Grundfos UP15-18 pull the water thru it ok?0 -
That data should be available
from the people that make the check valve. it's called the cv factor. The flow rate in GPM with a one psi drop.
Ideally you want the check on the discharge side of the circ. The 15-18 will also have a pump curve and the HX a pressure drop listing at various GPMs.
All these pieces of the puzzle will answer your question.
Is this a small DHW recirc flowing thru an isolation HX by chance?
hot rod
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The loop thru the on-demand
will need some serious pumping power. They usually have a fairly restrictive heat exchanger. I'd guess more like a 26-99 to move enough flow to get some of the capacity. i doubt that you will get the full capacity out of the heater with a "pumped flow." These units really aren't a good match for hydronic use. The small HX and low 80% efficiency, when firing, work against the initial "good price
Most of the manufacturers of those instantanous heaters have a flow chart available. What brand are you considering?
Glenn Sossin wrote a good post about this with a piping schematic back about 8/8/07 if you search the archives it may turn up.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements