Main vents

Brad White
Member Posts: 2,399
from a slug of steam-propelled water crashing up inside the vent and making scrap metal of it's delicate insides...
If you keep that in mind, (as I think you are) you can do the right thing.
I have seen it recommended to put an elbow or two between the vent and the main, (maybe a switch-back with it's own dead-end tee, thinking out loud?) and slow down the wave at least.
But with that approach, there are no guarantees. You really do want a wave, if it occurs, to pass harmlessly by, below your vent tapping. One whack at over 3 PSI is all it takes. Even lower pressures can generate some force above that with velocity and a good slug of water.
If you keep that in mind, (as I think you are) you can do the right thing.
I have seen it recommended to put an elbow or two between the vent and the main, (maybe a switch-back with it's own dead-end tee, thinking out loud?) and slow down the wave at least.
But with that approach, there are no guarantees. You really do want a wave, if it occurs, to pass harmlessly by, below your vent tapping. One whack at over 3 PSI is all it takes. Even lower pressures can generate some force above that with velocity and a good slug of water.
"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad
-Ernie White, my Dad
0
Comments
-
Main Vents
I just looked at a job where the main vents are installed at the end of the steam main in a tee with a 4" nipple. Dan says it shouldn't be there. He suggests cutting a tee in the main 15" from the end of the main. Is there a way I can move the vent without cutting the main pipe using elbows and nipples? Has anyone tried this with success?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
You could
drill and tap a hole in the side of the last radiator runout tee, and elbow up to your main vent. We do this all the time, and have never had a problem.
But we also see lots of vents installed like yours is, and they work fine as long as the pressure doesn't get too high.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements