Gas boiler problem
simply that the pilot needs cleaned. The change from standing pilot to intermittent should not have required any change of orifice size on the pilot. That is as long as the existing pilot was simply converted from a thermocouple to spark igniton retrofit.
Get a reputable gas service technician to come and service the unit and he or she should be able to solve the problem. A dirty pilot (yellow) will carbon up a small amount in and around the pilot. If you are having carboning greater than that then you have combustion problems and as Robert O'Brien posted get a combustion analysis done on the equipment. That should be done annually anyway.
Get a reputable gas service technician to come and service the unit and he or she should be able to solve the problem. A dirty pilot (yellow) will carbon up a small amount in and around the pilot. If you are having carboning greater than that then you have combustion problems and as Robert O'Brien posted get a combustion analysis done on the equipment. That should be done annually anyway.
0
Comments
-
Flame too yellow
We're told the pilot flame on our Burnham Independence boiler Model IN9N, installed in 1999, is too yellow. We changed the pilot from standing to intermittent in 12/03 and have had carbonation problems since. Any suggestions? Thanks so much!0 -
Get
somebody with a combustion analyzer in there.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
Boiler flame too yellow
Thanks so much for your advice.0 -
flame too yellow
Thanks for your advice!0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements