FVIR and power vented water heaters
Rich Kontny_3
Member Posts: 561
What make and where are they located ex: basement, first floor etc.
Rich K.
Rich K.
FVIR power vented problems
Has anyone run into problems with the power vented water heaters? the gas valves locking out or sensors failing ?
We have had serveral that lock out as the sensors are sensitve to humidity and temprature , some of the gas valves wont reset after lock out and must be replaced to get the water heater working ,
I was wondering about power supply how sensitive are these gas walves to power fluctuations , most of the failures seem to be in 1 corner of town0 -
We need more info
as to make model and whose control is being used on the water heater???0 -
the state and bradford white power vented models are bolth having premature failures within the firt months of start up. the gas valves are failing and none of the local wholesalers are carring the right parts for repair , we have 8 water heaters that are still waiting for parts 8 months later there still sitting is our shop because we used parts from them to repair installed water heaters .
there all missing the same parts.
State has the intelevenet gas contol from white rogers and B&W has a spark ignition from honeywell0 -
You mention it is in the one area of town, where do you work out of? What flash code is the control give? I have had good luck with BW's..
DB0 -
What are the numbers on those
controls from Honeywell and White Rodgers? I need that in order to help you out with what may be the problem.
By the way make sure the polarity is correct on all of those units!!!0 -
BW uses the honeywell spark control. I understand that the spark control is not polarity sensitive, unlike the hot surface controls with most furnaces0 -
Reverse Polarity
is a problem on any control system as when the polarity is reversed then the R and C terminals on the secondary of the transformer are reversed and this can cause problems as burner ground, MV/PV and 24 volt ground are the proving circuit for the flame rectification signal to prove flame.0 -
all of our installs are checke for polaity it was a problem when the first came out everyone got a tester
the most commem code on the state is first and last light shown and also the ignighter has failed , its usally the gas valve and not the igniter0
- 87K THE MAIN WALL
- 57 Biomass
- 115 Chimneys & Flues
- 5.7K Gas Heating
- 107 Geothermal
- 70 Pipe Deterioration
- 983 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 44 Industry Classes
- 48 Job Opportunities
