mcdonnell miller 67 series low water cut off
Parts are available for these, but given the age it is, and looking at <A HREF="http://www.mcdonnellmiller.com/pdf/install_instr/MM-815C.pdf"> MM recommended maintenance </A>, I would replace-it myself.<BR>Do NOT fool around with an old unreliable LWCO! <BR><BR>Dave
0
Comments
-
McDonnell Miller Series 67 Low Water Cut Off problem
Hello,
The mcdonnell miller 67 low water cut off valve on my steam boiler was receiving 120 V but only putting out 30 V. The BX switch had no continuity. The incoming hot is attached to terminal one and the "neutral" to terminal 2. However when I removed the BX switch and manually operated the lever on the back both of the circuits (terminal1 & 2 which relays the 120V to the 24V transformer), and (terminal3 & 4) tested positive for continuity.
The float lever didn't move but a little pressure freed it. Before that it was stuck in position so it kept the circuit(terminal 1&2) open. So I flushed it then filled it up a few times and the float raised and lowered properly with the water level.
I tried to remove the float assembly but it wouldn't budge.
Is the float assembly removable? If so do I need to remove it for inspection even though it worked during my test?
The blow down valve works but I could not get it out so I could better flush the float chamber? Does it come out and would I really need to do that?
Or did I solve the problem. The low water cut off is 10 years old.
Thanks
Matt
0 -
M&M 67
Matt, (wrote)
The low water cut off is 10 years old.
It has reached it's replacement interval, 10 years.
Replace or have replaced as whole assembly.
Linkage;
http://www.mcdonnellmiller.com/pdf/M&M/Product/Maint.pdf
HTH, db0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements