Optimum Boiler Sizing
Jay Zebryk
Member Posts: 16
Assuming my steam load calculations are correct, I need a boiler capable of generating 423 Square Feet of steam or 101,461 BTU's. The Utica boilers I've choosen are either 90,000 BTU (about 11% undersized) or 113,300 (about 12% oversized). Considering that Utica includes an allowance of 1.333 for "piping and pickup", which unit would be best? My concern about installing a slightly undersized unit is my full-time cellar workshop would now get too cold and require a radiator to make up for the lack of waste heat. Currently, all my cellar steam feeds are insulated with 1" fiberglass, and the boiler that I am replacing was "measured" by MassSave about ten years ago at 79%. It has no damper, however, and has a 6 inch flue pipe with a 12x12 inch draft box open at the bottom. The other factor of mention, is all my cellar windows (4) are old single pane types needing replacement as well.
boiler sizing
Go to the larger size. Undersizing is never a winning choice. Use the larger boiler and downfire it a little. Mt two cents worth.
- 87.4K THE MAIN WALL
- 167 Indoor-Air Quality