The installed boiler is a Dunkirk QL100 non-modulating condensing boiler w/3 fin tube zones and an indirect water heater zone. I am using the expandable Taco switching relay, and want to incorporate the Taco PC700 outdoor reset control. If I go this route, will the priority DHW feature of the switching relay override the tentative lower temp. set of the reset control allowing high temperature for the DWH? There is no reference in Taco literature addressing this. It is somewhat addressed in literature for their PC702 reset. This model reset control however is for a two stage boiler, but makes reference to domestic hot water demand output. (it's also $100.00 more)
Thanks in advance for any input you can offer.
Thanks in advance for any input you can offer.
0
Comments
-
Bypass reset curve on DHW demand
Connect the PC700-2 cable to the add-On interface on the Taco Zone Control. Ensure the Mode switch on the Zone Control is set to Reset.
You need to use any Taco Expandable Relay Unit (EXP model). Make sure indirect is hooked up to the priority zone. It will automatically bypass the reset curve on a DHW demand and boiler will fire to what ever the high limit is set at.0 -
Thank You Glenn...
Thank you Glenn, That was the explanation I was hoping to hear. You guys are great.
Jon0 -
Also
Look into the PC605 plug-in power-port card. It will only run the Priority for one hour and then shut off the priority. Nice protection in case of a bad circulator or air bound coil.
Scott
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Scott...
Thank you for reinforcing what I thought was a good purchase.
I actually ordered the PC605 (on backorder) and the PC600 for priority post purge. They both sounded like worthwhile investments. The job should all come together fairly soon.
Jon0 -
taco job
Hey Jon L --
Could you e-mail me some pictures when you're done. I'd love to use them in training. Thanks!0 -
I'm not a pro John, but...
I'd be happy to forward some pictures when done. Having seen your signature I'm sure your interest lies with my use of the Taco products. I'm a home Inspector by trade, and am helping my son with this install. You will be happy to know that your products seem to be the preferred choice locally. (Plattsburgh,NY) As well, they seem to be perfect for our job.
Armed with some pretty good basic knowledge, Dan's books, and advise from the experts at this site, the job has moved along quite smoothly.
Jon0 -
yes, DHW always over rides the reset control. The PC700-2, and the pc702 two boiler staging control both offer outdoor reset.Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements