Burnham PVG-4 Boiler Questions
Roland_4
Roland_4 Member Posts: 84
Date: October 07, 2007 06:14 PM
Author: Roland
Subject: Boiler question
Hi All, First off I want to thank you gentlemen(and if so,ladies) for your terrific help. As I've said preveously, I have a new Burnham PVG-4 Boiler. I have re-printed the installation manual and read it through a few times. Some information I cannot seem to find. What determines the boiler low temperature setting? At this time the heat function on the thermostat is turned off and only the DHW priority is active. When DHW is called for, the burner runs till the supply temp reaches 156*. When DHW is satisfied, the supply temp slowly drops to less than 100* sometimes as low as 70* if no DHW is called for,for an extended period of time. Does this not put a thermal strain on the boiler elements? Not to mention condensation?Also, when the heating season does start ( hard to imagin as the outdoor temp has been in the mid 80's for days in the New York City Suburbs no less). What will keep the boiler supply temp above the condensation point of approximately 135*? And how will my plan of installing and Out Door Reset affect the boiler operation Thanks again,Roland
Date: October 08, 2007 12:25 PM
Author: Glenn Sossin
Subject: There is no low limit
on this boiler. A low limit is typically found on boilers that have a tankless coil. It's used to maintain a minimum temperature in the boiler so when there is a demand for hot water, it will heat the flow of water through the coil.
As far as the temperatures your citing, there is thermostatic switch (aquastat) on your indirect that senses the water temperature in the tank. When the tank water temp drops below a certain value, it tells your boiler to turn on and send hot water into the indirect to reheat the water in the tank. Once this switch is satisfied, it turns off your boiler.
Based on the temperature readings you are giving, I assume your reading the tridicator gauge (temp gauge on the boiler). Your indirect is very well insulated. Depending on conditions, it will usually lose approx 1/2 - 1F per hour. If there is no call for hot water, the indirect tank may turn the boiler on 2-3 times a day for a few minutes.
The boiler and connected piping is not insulated like the indirect, and it can lose temperature much more quickly. That's why you saw temps as low as 70 but the indirect, being well insulated, still had sufficient hot water stored inside and did not turn on the boiler.
It really doesn't strain your boiler. Just because your boiler is sitting at 70 or 90 degrees is not a concern with respect to flue gas condensation unless it was on.
Flue gas condensation occurs when the flue gas come in contact with the cool surfaces in your chimney and vent piping. Two of the byproducts of combustion, sulfur dioxide and water can mix together forming an acidic condensate which will attack all the surfaces it comes in contact with including the boiler itself.
The more efficient the heating appliance, the lower the flue gas temperatures. The lower the flue temperature, the higher the potential for condensation to occur. This is why your boiler vents with stainless steel. Having the boiler sit there, not operating with a temperature under 135F does not cause this to occur.
When your boiler fires up, the return temperature will be a function of several conditions - the high limit, gpm, system efficiencies, heating load, heating cycles, stack temperature, etc. The condition you are trying to avoid is called sustained flue gas condensation - a situation where the flue gas temps are so low, condensing occurs on a continual basis.
Think of the tail pipe of a car. Ever notice in the cold weather, when the car has been running for a minute or two - the liquid dripping out of the tail pipe - thats condensation. But once the car is running for a while and the engine and exhaust pipes warm up, this goes away. Same thing for your boiler provided the flue gas temperature stays above the dew point of the exhaust gasses.
If your using an indoor outdoor reset with this boiler, the curve will have to be set such that sustained flue gas condensation doesn't occur. If you had a condensing boiler, designed for condensation, you might be able to have the low point of your reset curve at around 90F if you have radiant heat. You need to look at your radiation loads to know how to set your reset curve. Your contractor should be able to help you with this.
Hope this answered your questions
Good luck
Glenn
Date: October 08, 2007 01:54 PM
Author: Ken
Subject: When you write...
"Domestic priority" - may we assume you have an indirect domestic hot water maker, driven off a dedicated zone of the heating/boiler system?
If so, all's well - as is!
And no; all boilers are capable of going from ambient to limit all the time. There is no "thermal shock" per se, anymore than your coffee pot at ambient having 212F coffee/water drop into it every morning. Boilers are designed for that event, repeatedly.
Date: October 08, 2007 02:28 PM
Author: Glenn Stanton
Subject: Roland
As others have already stated, when a call for heat is encountered from either a zone of heat or the Indirect Water Heater, the boiler will turn on and fire up to the boiler's desired high limit setting. If the gauge reading you are seeing is the hottest the boiler is getting on the supply outlet, then either your boiler aquastat is set too low or the temperature gauge is a bit off. The boiler high limit should be and is most often set for 180°F to 190°F. You can check the setting by looking inside the boiler vestibule. You will see a control on the control panel with a silver wheel type dial with numbers. The setting opposite the pointer at the top should be set at 180°F to 190°F. The wheel will have a small semicircular bumpout on its rim at the 190°F setting.
While the burner is operating, you should expect to see it shut off when it reaches its high limit. The control has a fixed 15°F differential meaning it will stay off and cool down 15°F to approximately 165°F if it were set for 180°F. At this point you will hear it fire back up but the fan-proving and ignition sequence of this boiler takes about 45 seconds. During that time you could expect to see it drop down to 155°F or so and then swing back on up again. My advice would be to get your installer to check those settings and correct them. Operating the boiler at constant temperatures below 150°F can breed excessive flue gas condensation which may prove to be detrimental to the life of the boiler in the long run. When there is no call for heat the boiler simply does not run. This is referred to as "Cold Start". Depending on how long your "Off Cycle" is, you could expect to see it cool down to ambient room temperature if it stays off long enough. Hope this helps.
Glenn Stanton
Manager of Technical Development
Burnham Hydronics
U.S. Boiler Co., Inc.
Date: October 09, 2007 08:21 AM
Author: Roland
Subject: Burnham PVG-4 Boiler Question
Thank you to all who have responded to my questions. I greatly appreciate the in-depth answers. I have stated in a previous post that my new boiler came installed with a Argo ARM-2 switching relay with prioity. My aim is to have installed the companion DPM2 outdoor reset control.What will keep the ODR control from allowing the boiler to operate below the condensing temperature assuming it's function is to adjust the water temperature based on outdoor temperature. In other words, what sets the minimum temperature using the ODR control. I have limited knowledge of heating systems and prefer to leave this work to experianced (and licensed/insured)professionals. I would like to educate myself as much as possible as to the finer points of the systems operation. Roland.........
  • Roland_4
    Author: Roland
    Good luck
    Glenn
    Author: Ken
    Subject: Roland
    Glenn Stanton
    Burnham Hydronics
    Author: Roland
  • Roland_4
    Author: Roland
    Good luck
    Glenn
    Author: Ken
    Subject: Roland
    Glenn Stanton
    Burnham Hydronics
    Author: Roland