Y-strainer before main vent - 20 mesh OK?
Ken_40
Member Posts: 1,320
of that quote from Dan?
In the forty years I've worked on steam I have never seen a wye strainer before a main vent. Nor would I advise one now.
The water that would collect in the clean-out would be just like a puddle in the main.
The installation of main vent(s) at the end of the main is problematic. The solution is to mount the end-of-the-main vent at least 12" from the actual, physical "end" - on a tee. This prevents steam driven condensate from "crashing" into the tee - incorrectly how many did it - and shooting up with enough force to "toast" the vent's fragile guts; rendering the vent useless and leaking for the next 20 years.
Even the best of the dead men installed the vent tees at the end of the main, creating a bull-headed arrangement that was sure to blow the vent up in short order. Some even tried to stick a 12" nipp up to the coupled vent, to avoid this dynamic - to no avail.
Take a look at page 85 of TLAOSH.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=504&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
In the forty years I've worked on steam I have never seen a wye strainer before a main vent. Nor would I advise one now.
The water that would collect in the clean-out would be just like a puddle in the main.
The installation of main vent(s) at the end of the main is problematic. The solution is to mount the end-of-the-main vent at least 12" from the actual, physical "end" - on a tee. This prevents steam driven condensate from "crashing" into the tee - incorrectly how many did it - and shooting up with enough force to "toast" the vent's fragile guts; rendering the vent useless and leaking for the next 20 years.
Even the best of the dead men installed the vent tees at the end of the main, creating a bull-headed arrangement that was sure to blow the vent up in short order. Some even tried to stick a 12" nipp up to the coupled vent, to avoid this dynamic - to no avail.
Take a look at page 85 of TLAOSH.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=504&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Last minute question
Well, my boiler replacement is scheduled to start Monday, and I have a last minute question. Last minute jitters too.
The exisiting mains never had a vent, so we're adding one. I saw Dan's advice on using a Y-strainer to protect it. Is the (apparently standard) "20 mesh" OK?
0 -
if you use a wye strainer
it will have to be vertical up..you may or may not have room for this..i never seem to.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
The source...
http://www.heatinghelp.com/newsletter.cfm?Id=165
I beleive the suggestion is put the y strainer near the end of the nipple.
Even though I will probably end up without a y-strainer--for me to bring this up with my installer feels like extreme micromanagement--I'm still curious...will 20 mesh be effective in this situation or do you go finer?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements