Firing rate confusion
Jim Franklin
Member Posts: 170
Hey, all the numbers work now..
Thanks Ken. Looks like I have 102,844 BTU available at 82.5% efficiency. Which nicely covers my 95,677 BTU needs (radiation + 1.33 pickup).
jim
Thanks Ken. Looks like I have 102,844 BTU available at 82.5% efficiency. Which nicely covers my 95,677 BTU needs (radiation + 1.33 pickup).
jim
0
Comments
-
I have a Dunkirk 3ES1.35 which has an input of 189,000, output 156,000 BTU at 1.35 gph. If oil has 190,000 BTU/gal, why isn't the firing rate close to 1 gph?
The current nozzle in there is a .75, but running at 140 psi, so do I really have 1.4 * .75 = 1.05 gph firing rate? If so, how do I calc the BTUs available to me?
My oil co was out today looking at my poorly piped header and their conclusion for the slow heating was that I'm way underfired. I have 299' of radiation and this system is rated for 488 at that 1.35 gph, so I need to find out how close I am with the current firing rate.
thanks,
jim0 -
oil only has roughly 140k btu per gallon.
.75 @ 140psi = .89gph @ 140k btu per gallon = firing rate of 124,600 btu/hr.0 -
Have you
properly vented and insulated your steam mains?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Insulated, not yet, working on the header rebuild. I know that's attributing significantly to the slow progression to the mains.
Venting - I think so. 1.4 cf of mains into 2 Gorton #1s is plenty by my numbers. Would you agree?
jim0 -
At 3 ounces
that would work fine. You can always add more if needed. Lately I've been sizing main vents at 1 ounce though, it affords more of a differential between venting the mains and venting the radiators.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Efficiency not 82%
Sold Dunkirk and I do not believe that boiler is designed to operate that low of input at all. Regardless, you will be lucky to be operating at 50% efficiency at that firing rate. Forget the 82% because the actual firing efficiency of oil can only reach about 74% to 75% if fired perfectly which would be about 4% O2 or 12% CO2.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements