Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
6\" boiler and DHW heater into 5.5\" flue liner

Techman
Member Posts: 2,143
Oil or gas? Priority control? BTU's of each?Elbows on each? Distance from appliance's to chimney? Interior or exteroir chimney?Height from floor of boiler room to top of chimney?Is boiler room conditioned?
0
Comments
-
Would you do it?
It's been proposed, and I am dubious.0 -
So it's feasible...
I think I have my answer. It can be done if conditions allow. By the way: gas, no priority control, approx 118,000 BTU on boiler, heater unknown. Elbows on both, appliances within 6 ft., exterior chimney height at least 16 ft. Boiler in unfinished basement, no radiators or A/C.0 -
Possible
Catogory 1-2-3-4 on each appliance also ?0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 940 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements