scaling copper to pex
Georg
Member Posts: 8
Is it correct that I need 2 times the feet of head for 3/4'' pex than for 3/4'' copper?
If I understand the system curve correctly, the required head decreases with the pipe area squared, or the diameter to the power of 4. I measured the inner diameter of copper-M to be about 13/16'', whereas 3/4 pex only has 11/16''. And (13/11)^4 is approximately 2.
Is the difference between pex and copper really that large?
If I understand the system curve correctly, the required head decreases with the pipe area squared, or the diameter to the power of 4. I measured the inner diameter of copper-M to be about 13/16'', whereas 3/4 pex only has 11/16''. And (13/11)^4 is approximately 2.
Is the difference between pex and copper really that large?
0
Comments
-
Check the ID of the pex fittings...waaay less than the pipe...Wirsbo expands, but standard crimp pex ftgs are the same ID as one size smaller copper...or slightly less.
TimJust a guy running some pipes.0 -
To a certain point
That's correct. But, a typical pex run will have virtually no fittings which add considerably on the copper side. When using pex you're usually dealing with what amounts to a straight run of tube.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements