Expansion tank location

Jim P
Jim P Member Posts: 29
I always pipe my boilers following the "pumping away" layout. Following this layout, can you remotely install the expansion tank (aprox 3-4feet away)? I will still be tying the expansion tank in under the air sccop and water feed, but just pipe it furter away.



Jim

Comments

  • Al Letellier_9
    Al Letellier_9 Member Posts: 929
    xtank piping

    It's done all the time with floor mounted tanks. Shouldn't be a problem as long as you don't get carried away. Make sure to hang the tank from the threaded connection. Don't lay it flat or upside down.
  • Joey B_2
    Joey B_2 Member Posts: 24


    Why wouldnt you pipe them upside down or sideways? I see it all the time, I always figured it didn't really matter.