gpm in pipes

Brendan_4
Member Posts: 12
Ken That is a lot of pressure for a 22' water colum
0
Comments
-
gpm in pipes
how many gpm can a 1-1/4" cu pipe type L deliver with 50 psi0 -
Alot!
I'm guessing (too lazy to do your homework);-o) it to be in the neighborhood of 50 GPM. That assumes there is no length to this tube, and no elevation of a few floors/feet - which has a huge impact on the number you seek.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
distance - assuming L copper
It is a function of friction. If we start at 50psi, and 50 gpm, travel 100ft straight in 11/4L copper, there would be a 18.94 ft of head loss. This would mean you would have a pressure drop of approx 8 psi. So you would have your 50 gpm through the 100ft of L tubing but the pressure at the end would be approximately 42psi - not the 50 you started with. Its called pressure drop.
Hope that helps you. See attachment0 -
Re-read the question.
He does not have 50 GPM's. He wants to know how many GPM's he could deliver @ 50# of pressure thru an 1-1/4" pipe.
Think of it this way Glenn, he has a very short piece of 1-1/4" 'L' tubing (providing virtually no friction loss) punched thru the wall of a dam. The hole and enclosed pipe is 21.7 feet below the resevoir's surface, which creates 50 p.s.i. static pressure.
How many gallons of water will shoot out of the stub a minute?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
In other words
The answer, as always, is....... It depends.0 -
gpm
On a water service line it all begins with the size of your water meter. For example, an 1 1/4 line with a 1 inch meter will deliver 20gpm at 50 psi static pressure, figuring a line 75 feet long. Call A.O. Smith tech. line for sizing tables. 1-800-527-1953.There was an error rendering this rich post.
0 -
Flow
I understood the question, but I didn't think he understood the factors, which is why included the friction loss table. The answer is 402 gpm according to a Fairbanks valve table I have. See attachment0 -
You said that right! If this is a city system, it's the meter size more than anything that limits flow. Connect a 1 1/4" entrance to a typical 5/8" residential water meter and you won't get much more flow than through the typical 3/4" entrance.0 -
That's why
I didn't post the real answer of 402 gallons based on the conditions Ken was menntioned. Hopefully, Richard realizes now, there is a lot more involved in answering his question.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements