Pipe Noise

Joe Mattiello
Member Posts: 735
Apparently, you have velocity issues; and you validated my assessment by closing down on a ball valve slowing down the flow which resolved the noise concerns. Additionally, high velocity can contribute to erosion issues.
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions
0
Comments
-
Pipe Noise
I have a new installation that is creating a noise throughout the system shortly after the circulator starts.
Taco 007/ supply side pump / 2 3/4 zones / Spiro vent / baseboard heat.
The noise will stop if I shut off ball valve on one return.
Systen press 12 lb. ???
0 -
Respectfully, another view
I see closing of one of the ball valves as increasing the flow in the remaining zones. Consider as an extreme if one closed all but one zone, the velocity would rise in the remaining zone.
If the velocity was caused in the one zone you throttled, that may be part of it, perhaps the one zone with less resistance (hence more flow) than the others.
That it is "throughout" tells me it *might* be velocity at some level (water transmits that pretty well, being incompressible), thus causing vibration. But I would want to know more.
I would need more information, starting with, "What does the noise sound like?". Rushing water? Gurgling air? Creaking? Show tunes by a Judy Garland impersonator?
That the noise starts "shortly after" as opposed to "immediately after" (if there is a difference in terms here) has me thinking that it might be a function of expansion noises. What temperature is being run?
Again, only guessing without narrowing down the type of noise and time from circulator start-up.
Just another view of things, that's all."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
noise
Abit less techy...how about harmonics? Pipes touching anywhere?? Just a thought. jw0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 939 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements