Baseboard in steam application.

Steamhead (in transit)
Member Posts: 6,688
they only have water ratings- at 220° (pretty close to steam) the 7-inch is 620 BTU per foot and the 10-inch is 890. These translate to 2.58 and 3.7 square feet EDR on steam.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Baseboard in steam application.
Hi,
I am in need of some help. I am loading out a house to properly size the new steam boiler and I have run into some old burnham "Base Ray" baseboard radiators. I have been in the EDR book and can find nothing in the Burnham section on these. I have two heights. one is 6 7/8" high and the other is 9 7/8" high. Does anyone know the EDR per foot on these?
Thanks
Tim0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements