Diverter T for pex ?
Georg
Member Posts: 8
Is it possible to use diverter T for pex? I was told that copper diverter Ts (3/4'' to 1/2'') could be connected to 3/4 pex fittings.
I am worried that the inner diameter of the copper diverter T is not very much less than that of the 3/4 pex fitting, and that the pressure drop will therefore not be sufficient to get good flow through the radiators.
I am worried that the inner diameter of the copper diverter T is not very much less than that of the 3/4 pex fitting, and that the pressure drop will therefore not be sufficient to get good flow through the radiators.
0
Comments
-
Try this
Try using 3/4 x 1/2 x 1/2 Pex Tees (2) with 1/2 in the middle, we have been sucessfull in the past to supply kickspace heaters on 3/4" hydronic loops.0
This discussion has been closed.