I think we have a winner!!!
and very very common, check-out their site, I`m sure they`ll have what you need.<BR><BR>Dave
0
Comments
-
Looked at this today. When 1 or 2 call for heat, both boilers fire, even though one does 1&2 and the other 3&4. When 4 calls, the valve opens and it only gets heat if 1 or 2 happen to be calling. Will not fire boiler. 3 does nothing at all. left boiler kettles bad and moans when at temp. Will be repiping soon. These are the same guys who brought you the other beauty pictured...
Enjoy, TimJust a guy running some pipes.0 -
Can anyone suggest a good 2-stage boiler control? I am putting these guys in parallel on the same pri loop, and a P/S setup, with the ZV's off that. I will also be using a differential pressure bypass.
Thanks, TimJust a guy running some pipes.0 -
Tekmar
Tim, go wit ha tekmar 262 and a taco zvc relay for the zone valves. The Tekmar has domestic hot water on priority so if you add an indirect later on0 -
Is that a taco zone valve controller? Have not heard of that one...I typically like pumps, but the ZV's are there already.
TJust a guy running some pipes.0 -
Are those hour meters
on the ZV's? By far the most confusing zone valve you will ever wire
You have one of the best tekmar reps around right there in Salt Lake. Mike or Dave at Lundquist Sales.
You need to meet the team at Hydronic Supply LLC at 2195 s West Temple. Hands down the most knowledgable supplier in the valley. Dave Hill, Bill McDonald, or Frank. They know copper boilers very wellI believe they are tekmar dealers also.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
yes
It is a taco zone valve control. Makes the job look nicer and you can wire it up to 6 zones with 1 control. They also come with a priority switch.0 -
I shop a lot at Lundquist for danfoss & tekmar ( now at 2425 S Progress Dr.), and Gritton for B&G. My local Laars shop is Midgley Heuber. This install is a total nightmare. I think having both boilers on one pri loop is the ticket, especially having them staged. Both are oversized, and having the larger do most of the work, and the second fill in at peak demand is the best bet.Just a guy running some pipes.0 -
Second boiler vent
Hi Tim,
I'll second the suggestion to use the Tekmar 262 with these boilers. Call myself or Bill at the factory if you have any questions on the wiring to the boilers.
And please take the old Mini Therm I draft hood off of the Mini Therm II integral draft diveter (the second boiler in the photo)and replace it with a piece of pipe, and move the vent damper down where it belongs.
You may also want to consider type B vent for the installation. I'm surprised that the vents don't condense.
Sincerely,
Paul Bock, Laars Heating Systems Co.
0 -
I have sent Bill Marchant an email with photos regarding this install. I did put in my estimate to remove the draft hood and fix the vent. There are signs of the right boiler condensing. See photo. There is white powder and rusty flakes falling out of the old draft hood. I really like these mini therms, but they MUST be piped right.Just a guy running some pipes.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements