I think we have a winner!!!

and very very common, check-out their site, I`m sure they`ll have what you need.<BR><BR>Dave

Comments

  • Timco
    Timco Member Posts: 3,040


    Looked at this today. When 1 or 2 call for heat, both boilers fire, even though one does 1&2 and the other 3&4. When 4 calls, the valve opens and it only gets heat if 1 or 2 happen to be calling. Will not fire boiler. 3 does nothing at all. left boiler kettles bad and moans when at temp. Will be repiping soon. These are the same guys who brought you the other beauty pictured...

    Enjoy, Tim
    Just a guy running some pipes.
  • Timco
    Timco Member Posts: 3,040


    Can anyone suggest a good 2-stage boiler control? I am putting these guys in parallel on the same pri loop, and a P/S setup, with the ZV's off that. I will also be using a differential pressure bypass.

    Thanks, Tim
    Just a guy running some pipes.
  • Tekmar

    Tim, go wit ha tekmar 262 and a taco zvc relay for the zone valves. The Tekmar has domestic hot water on priority so if you add an indirect later on
  • Timco
    Timco Member Posts: 3,040


    Is that a taco zone valve controller? Have not heard of that one...I typically like pumps, but the ZV's are there already.

    T
    Just a guy running some pipes.
  • hot_rod
    hot_rod Member Posts: 24,580
    Are those hour meters

    on the ZV's? By far the most confusing zone valve you will ever wire :)

    You have one of the best tekmar reps around right there in Salt Lake. Mike or Dave at Lundquist Sales.

    You need to meet the team at Hydronic Supply LLC at 2195 s West Temple. Hands down the most knowledgable supplier in the valley. Dave Hill, Bill McDonald, or Frank. They know copper boilers very well :) I believe they are tekmar dealers also.

    hot rod
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • yes

    It is a taco zone valve control. Makes the job look nicer and you can wire it up to 6 zones with 1 control. They also come with a priority switch.
  • Timco
    Timco Member Posts: 3,040


    I shop a lot at Lundquist for danfoss & tekmar ( now at 2425 S Progress Dr.), and Gritton for B&G. My local Laars shop is Midgley Heuber. This install is a total nightmare. I think having both boilers on one pri loop is the ticket, especially having them staged. Both are oversized, and having the larger do most of the work, and the second fill in at peak demand is the best bet.
    Just a guy running some pipes.
  • Paul B._2
    Paul B._2 Member Posts: 62
    Second boiler vent

    Hi Tim,

    I'll second the suggestion to use the Tekmar 262 with these boilers. Call myself or Bill at the factory if you have any questions on the wiring to the boilers.

    And please take the old Mini Therm I draft hood off of the Mini Therm II integral draft diveter (the second boiler in the photo)and replace it with a piece of pipe, and move the vent damper down where it belongs.

    You may also want to consider type B vent for the installation. I'm surprised that the vents don't condense.

    Sincerely,

    Paul Bock, Laars Heating Systems Co.

  • Timco
    Timco Member Posts: 3,040


    I have sent Bill Marchant an email with photos regarding this install. I did put in my estimate to remove the draft hood and fix the vent. There are signs of the right boiler condensing. See photo. There is white powder and rusty flakes falling out of the old draft hood. I really like these mini therms, but they MUST be piped right.
    Just a guy running some pipes.