Need help redesigning steam/FHW system
Options
Jim Franklin
Member Posts: 170
I need an aquastat to limit my steamer to 180 when there's a call for FHW or DHW. Any particular model recommended for this? Where does it usually get installed? I have a Dunkirk ES1.35 with a tankless coil (not used) and the hot water zones use a tapping in this plate. Seems like a good candidate to me.
Any recommendations on a DHW indirect circulator that'll push 10gpm at 8.7' head through 1" pipe? I looked at Taco and Grundfos and found a few that'll work. Should I get an integral flow check? If not I'll need to add the check valve's loss to that 8.7'.
I need to install roughly 8000 BTUs of baseboard or panels in a new 2nd story (20' above water line with panels). With the boiler in the basement, is there a better way to go than using boiler water? I'd be up for purchasing a tank & echanger setup. There's currently a small addition being heated by a FHW zone using boiler water and it's always been problematic. I'd like to do the FHW zones the *right* way (more steam is out).
Many thanks for whatever guidance you can give.
jim
Any recommendations on a DHW indirect circulator that'll push 10gpm at 8.7' head through 1" pipe? I looked at Taco and Grundfos and found a few that'll work. Should I get an integral flow check? If not I'll need to add the check valve's loss to that 8.7'.
I need to install roughly 8000 BTUs of baseboard or panels in a new 2nd story (20' above water line with panels). With the boiler in the basement, is there a better way to go than using boiler water? I'd be up for purchasing a tank & echanger setup. There's currently a small addition being heated by a FHW zone using boiler water and it's always been problematic. I'd like to do the FHW zones the *right* way (more steam is out).
Many thanks for whatever guidance you can give.
jim
0
Comments
-
advice
I use Honeyell immersion aquastats with good results. I would recommend a tank type heat exchanger for the FHW and use a bronze pump without flow check between the boiler and the tank. I don't think a standard IFC pump internal flow check would stand up to the higher temp for very long.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements