Boiler drops pressure when circ runs

Brad White
Member Posts: 2,399
The circulator is pumping toward the expansion tank (through the boiler incidentally) and that is the root of it.
Move the expansion tank to the suction side of the circulator (make it an Extrol or other diaphragm type) as you said, and be done with it.
Move the expansion tank to the suction side of the circulator (make it an Extrol or other diaphragm type) as you said, and be done with it.
"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad
-Ernie White, my Dad
0
Comments
-
Boilerdrops pressure when circ pm runs.
Customer called with water on the floor. Oil fired boiler with domestic hot water coil. Boiler was at140 degrees. When circ ran on call for heat boiler pressure dropped to zero or below. Expansion tank seemed to be full. When heat call ended, boiler heated to 160 degrees, pressure rose to 30 lbs., and blew off at safety valve. Component arrangement: Circ on return, water fill 2" down stream of circ, boiler, 5" of riser pipe out top of boiler supply, combo flow check and 1/2" copper expansion tank line to tank overhead. Seems like th circ should be pumping away from that tank?? And that the tank and water fill should be hooked up at the same place??? Can I use this same expansion tank??? Or should I go with spiro vent and extrol 60??0 -
Pressure
In addition to pumping away from the expansion tank it also sounds to me like the expansion tank has failed. If this is a compression tank, as Brad said, replace it with a bladder tank on the suction side of the pump.0 -
What happened when you drained the expansion tank?
You did drain the expansion tank and run another cycle, didn't you?0 -
Adding the diaghram type tank and piping it and the fill line in the proper orientation is what I proposed to do.0 -
How does a compressipon type expansion tank fail, by leaking correct?0 -
Wellll; The homeowner claimed he emptied it, but it was full when I got their. Someone had recently replaced this boiler; homeowner just purchased the home ( I believe this happened when they began using the heat.)0 -
Bet there was no way
for air to re-enter the tank when he "emptied" it.
I sometimes wonder if switching to a diaphragm tank is really the best way to go, given that the diaphragm is a moving part and will eventually fail. A plain steel tank fed from an air separator and thru an Airtrol fitting with proper piping between the two, won't waterlog. And it has no moving parts.
Something to think about, eh?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Go along with Brads thoughts...
He is saying it clearly.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements