1 1/4\"dry returns to 1 1/4' wet returns
Brad White
Member Posts: 2,399
a wet return of a given size will move about twice the capacity of a dry return of the same size, but as Jim said, you have to know what the load is in the first place.
If it works now "sort of" then performance should improve. However the path in total only has the capacity of the most sluggish section. In other words, if half is left as a dry return, that will define the return rate.
Wet returns are prone to clogging over time given that they are the low points of a system where things tend to settle.
If it works now "sort of" then performance should improve. However the path in total only has the capacity of the most sluggish section. In other words, if half is left as a dry return, that will define the return rate.
Wet returns are prone to clogging over time given that they are the low points of a system where things tend to settle.
"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad
-Ernie White, my Dad
0
Comments
-
Dry returns to wet - does pipe size need to increase
can a 1 1/4" dry return be dropped to the floor and properly function as a 1 1/4" wet return? Does it need to be larger such as 1 1/2"?0 -
Returns
That is the load of the boiler & how many returns are there0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements