Stema Fin-tube question
Mario_3
Member Posts: 1
I have a 6ft length on 1 1/4 steel fin tube radiator on a one pipe steam system. What options do I have for replacement? I would like to get similar EDR numbers/ ANy input out there??
0
Comments
-
Many options
Get to the manufacturer's website and see how many BTU's that fin-tube six-footer puts out when steam is the energy source (as opposed to water) This is typically the output rating stated at 215F - if not specifically stated for steam.
Sun-Rad type radiators are still available, as are tube/column type. CIBB is another option. Simply "convert" BTU's (if required) to EDR by dividing BTU's by 240; then, look at alternative forms and match the BTU/EDR as needed. If the fin-tube that's there, is adequate, make no BTU/EDR "adjustments" If the area seems cool or warmer than desired; now's the time to make an adjustment.
Let us know how it all works out
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements