Stema Fin-tube question

Mario_3
Member Posts: 1
I have a 6ft length on 1 1/4 steel fin tube radiator on a one pipe steam system. What options do I have for replacement? I would like to get similar EDR numbers/ ANy input out there??
0
Comments
-
Many options
Get to the manufacturer's website and see how many BTU's that fin-tube six-footer puts out when steam is the energy source (as opposed to water) This is typically the output rating stated at 215F - if not specifically stated for steam.
Sun-Rad type radiators are still available, as are tube/column type. CIBB is another option. Simply "convert" BTU's (if required) to EDR by dividing BTU's by 240; then, look at alternative forms and match the BTU/EDR as needed. If the fin-tube that's there, is adequate, make no BTU/EDR "adjustments" If the area seems cool or warmer than desired; now's the time to make an adjustment.
Let us know how it all works out
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 975 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements